Warning: Repairing a UPS is not for beginners. There are many high voltage components that can seriously electrocute you.
3 years ago I bought a used APC UPS BR1000MS (1000VA, pure sine wave). I have it connected to all my media center devices (PC, TV, Receiver) but it rarely gets above 50% its rated power delivery. About a month ago, while I was watching a video, I got a power outage and immediately I heard a loud pop from the UPS. Everything connected to the UPS lost power, and the error code F02 appeared on the UPS LCD.
Unfortunately F02 is somewhat common and it's a death sentence for an APC UPS. APC doesn't say what problem it indicates, but it's clear from looking at posts that it indicates a hardware problem. Some threads mention burning smells, smoke, and in one case fire. Even after a hardware revision, there are posts of people still getting the error.
Just for good measure I tried all the reset troubleshooting steps and even tried using a known-good battery but to no avail. The UPS is long out of warranty so there won't be any help from APC. A local repair shop quoted me $100 just to diagnose the thing and a minimum of $50 if they deemed it repairable. I could get a whole UPS for that price so I decided I would diagnose it myself.
I started by taking the plastic shell apart and doing a basic inspection of the circuit board. The problem immediately seemed clear, one of the mosfets had exploded!
Mosfet model: IRFB7440 IOR P806J JK GO
More pictures: https://imgur.com/a/LrQykdg
While I waited for a replacement mosfet from Digikey, I noted the highest voltage the board used was around 400v. I got some Class 00 gloves which are rated to 500v AC and 750v DC. They're very bulky and difficult to work in, but I couldn't avoid touching the circuit board in order to replace the mosfet. After the parts arrived I spent 4 hours performing the replacement and putting everything back together. I plugged in the UPS, connected the battery, turned it on, and it worked! For only 5 seconds. I heard another pop and the dreaded F02 error reappeared. https://youtu.be/aKos3EM3o2Y
I expected another broken mosfet but surprisingly they were all intact. Since the pop happened just as the UPS switched to battery mode, I suspect there's a bad relay/contactor. This could explain why some users smelled smoke. If a battery relay got welded closed or shorted, I could easily see the plastic melting. There's two 30A internal fuses but the relays are only rated for 16A so I don't know what purpose the fuses serve!
I guess the next step is to figure out which relay is broken. It's such a hassle to safely handle the circuit board I don't know when I'll get around to it.
3 years ago I bought a used APC UPS BR1000MS (1000VA, pure sine wave). I have it connected to all my media center devices (PC, TV, Receiver) but it rarely gets above 50% its rated power delivery. About a month ago, while I was watching a video, I got a power outage and immediately I heard a loud pop from the UPS. Everything connected to the UPS lost power, and the error code F02 appeared on the UPS LCD.
Unfortunately F02 is somewhat common and it's a death sentence for an APC UPS. APC doesn't say what problem it indicates, but it's clear from looking at posts that it indicates a hardware problem. Some threads mention burning smells, smoke, and in one case fire. Even after a hardware revision, there are posts of people still getting the error.
Just for good measure I tried all the reset troubleshooting steps and even tried using a known-good battery but to no avail. The UPS is long out of warranty so there won't be any help from APC. A local repair shop quoted me $100 just to diagnose the thing and a minimum of $50 if they deemed it repairable. I could get a whole UPS for that price so I decided I would diagnose it myself.
I started by taking the plastic shell apart and doing a basic inspection of the circuit board. The problem immediately seemed clear, one of the mosfets had exploded!
Mosfet model: IRFB7440 IOR P806J JK GO
More pictures: https://imgur.com/a/LrQykdg
While I waited for a replacement mosfet from Digikey, I noted the highest voltage the board used was around 400v. I got some Class 00 gloves which are rated to 500v AC and 750v DC. They're very bulky and difficult to work in, but I couldn't avoid touching the circuit board in order to replace the mosfet. After the parts arrived I spent 4 hours performing the replacement and putting everything back together. I plugged in the UPS, connected the battery, turned it on, and it worked! For only 5 seconds. I heard another pop and the dreaded F02 error reappeared. https://youtu.be/aKos3EM3o2Y
I expected another broken mosfet but surprisingly they were all intact. Since the pop happened just as the UPS switched to battery mode, I suspect there's a bad relay/contactor. This could explain why some users smelled smoke. If a battery relay got welded closed or shorted, I could easily see the plastic melting. There's two 30A internal fuses but the relays are only rated for 16A so I don't know what purpose the fuses serve!
I guess the next step is to figure out which relay is broken. It's such a hassle to safely handle the circuit board I don't know when I'll get around to it.